Delayed alerts (with adjustable delay) in business Started plan

Hello,

Could someone explain what are Delayed alerts (with adjustable delay) in business Started plan?

I’m actually using Ruuvi sensors to monitor freezers (down to -30ºC) in a supermarket. Those equipements have a defrosting mecanisme that let the equipment raise upto 19-25ºC every 4 hours or so in order to remove ice within the fidge.

I would like alerts that give notifications when the temperature is above or below a certain value during x minutes. Meaning that if the temperature is higher that 15ºC more that 20 minutes the equipement is having a problem, but less that 20 minutes it is in defreezing mode and everything is fine.

Is there such alert notification availble ? Is it the meaning of “Delayed alert”?

Thx for your help

Hello,

This is exactly what delayed alerts do, we developed them to avoid false triggers on fridge / freezer defrosting cycles.

1 Like

Thank you, great!